Sqe survey on fixed co2 system, explain co2 cylinder testing procedures and what are the items you must check while doing test.

Answer

Scope of SEQ Survey on Fixed CO2​ System

During an SEQ survey, the Surveyor and Chief Engineer inspect the entire installation across four main zones:

  1. CO2​ Central Battery Room:
    • Ventilation: Mechanical exhaust ventilation working properly (fans drawing from the bottom of the room, as CO2​ is heavier than air).
    • Illumination & Access: Explosion-proof light fittings, clear egress paths, and self-closing door with keys kept in a break-glass box nearby.
    • Environment: Room temperature maintained below 55°C.
  2. Distribution Piping & Discharge Nozzles:
    • Blow-Through Test: Annual blow-through of distribution lines using dry compressed air or nitrogen to ensure piping is clear of debris/rust and nozzles are unobstructed.
    • Section Control Valves: Visual inspection and manual operation of manifold directional valves, ensuring clear markings identifying the protected spaces.
  3. Pilot Control & Alarm Cabinets:
    • Remote Release Cabinets: Checking microswitches that trigger pre-discharge visual/audible alarms and shut down E/R ventilation fans, fuel pumps, and fire dampers upon opening the cabinet door.
    • Pilot Cylinders: Checking N2​ or CO2​ pilot gas cylinder pressures, operating wires, pneumatically operated actuators, and manual trip handles.
  4. Safety Mechanisms:
    • Pressure Relief Valves (PRVs): Verifying PRVs on the discharge manifold and pilot lines are free of corrosion and calibrated.
    • Safety Interlocks: Verifying two-step release operation (Step 1: Open control cabinet / stop ventilation; Step 2: Open pilot/master valve and discharge gas).

2. CO2​ Cylinder Testing & Maintenance Procedures

The maintenance and testing of high-pressure seamless steel CO2​ cylinders follow strict intervals per MSC.1/Circ.1318/Rev.1:

Monthly Visual & Pressure Checks (Gauges / Leakage)

│

▼

Annual Level Check (Ultrasonic / Weighing - Max 10% Loss)

│

▼

10-Year Hydrostatic Test (100% Battery Tested / Min 10% at 10 Yrs)

│

▼

Cylinder Inspection, Valve Refurbishment & Refilling

A. Annual Contents / Level Verification

B. Hydrostatic Pressure Testing (Hydraulic Stretch Test)

the following parameters must be verified and documented: