a major repairs on boiler completed . After completion what is duty of chief engineer or class requirements??

Answer

When extensive repairs (e.g., replacement of generating/water-wall tubes, combustion chamber plating repairs, or furnace re-welding) are completed, a strict protocol under Class and national rules (Indian MS Act, 2025) must be followed before recommissioning.

Class Requirements & Surveys

  1. Approved Welder & Materials: Ensure all welding was conducted by a Class-certified pressure vessel welder using Class-approved low-hydrogen electrodes with matching material test certificates (MTC).

  2. Non-Destructive Testing (NDT): Prior to any pressure testing, Class mandates Radiographic Testing (RT) or Ultrasonic Testing (UT) of the newly executed structural welds to verify zero internal volumetric defects or inclusions.

  3. Hydraulic Test (Hydro-test):

    • Class requires the boiler to undergo a hydrostatic pressure test.

    • Test Pressure: Typically conducted at 1.5 times the maximum allowable working pressure (MAWP) of the boiler.

    • Conditions: Water temperature must be maintained above the brittle fracture threshold (typically between 30C and 40C). The pressure must be held steady for at least 30 minutes while the Class Surveyor examines all tubes, welds, and tube plate expansions for distortion or weeping.

Duties of the Chief Engineer